Feb 15, 2011 #1 GFCME Mechanical Joined Feb 15, 2011 Messages 1 Location US AS PER ASHRAE 90.1, IS IT ACCEPTABLE TO SELECT A MOTOR TO THE NEXT LARGER MOTOR SIZE WHEN THE 90.1 CALCULATED MOTOR SIZE FALLS BETWEEN TWO STANDARD HORSEPOWER SIZES?
AS PER ASHRAE 90.1, IS IT ACCEPTABLE TO SELECT A MOTOR TO THE NEXT LARGER MOTOR SIZE WHEN THE 90.1 CALCULATED MOTOR SIZE FALLS BETWEEN TWO STANDARD HORSEPOWER SIZES?
Feb 16, 2011 1 #2 ChrisConley Mechanical Joined May 13, 2002 Messages 975 Location CA Yes. Upvote 0 Downvote