ASCE 7-05 table 12.8-2 1

Status
Not open for further replies.

SteelPE

Structural
Mar 9, 2006
2,759
I design mostly small steel framed buildings (less than three stories in height) nothing glamorous. When checking seismic loads I typically use a R=3 systems to avoid the seismic requirements (mostly the connection forces). Recently I designed a 3 story office building that required the use of an eccentric braced frame system. Again, to avoid the seismic requirements I used a R=3 system. My question is in relation to table 12.8-2 of ASCE 7-05. As I read this table, I could use a Ct = 0.03 for this system as there is nothing in the table that says the Eccentrically braced steel frames must be in compliance with the seismic provisions. Is this interpretation correct?
 
Replies continue below

Recommended for you

Based on Table 12.2-1 (B1 or B2), R is 7 or 8 for your framing system. Why R=3?
 
R=3 so we can opt out of the seismic provisions (as indicated in the OP). So in this instance we have a system utilizing R=3 but the structural system is eccentrically braced frames. I selected this system such that I don't have to be in compliance with the detailing requirements of the seismic provisions. I am questioning if the framed need to be detailed in accordance with section 14.1 in order to use Ct=0.03 in table 12.8-2.
 
Check to see if your lateral system can be classified as "System not specifically detailed for seismic resistance" (check the exact wording, but I believe that's what its called). In that case, your braced frames or moment frames can take any configuration, even if it happens to be an EBF and you can use R=3. However, if you DETAIL it according to the seismic provisions, than you need to use the appropriate R=7 or 8.
 
Here is the paragraph to which MotorCity refers:

14.1.2 Seismic Design Categories B and C. Steel structures assigned
to Seismic Design Category B or C shall be of any construction
permitted by the reference documents in Section 14.1.1.
An R factor as set forth in Table 12.2-1 is permitted where the
structure is designed and detailed in accordance with the requirements
of AISC 341 for structural steel buildings and AISI Lateral
for light-framed cold-formed steel construction. Systems not detailed
in accordance with AISC 341 or AISI Lateral shall use the
R factor designated for “Structural steel systems not specifically
detailed for seismic resistance” in Table 12.2-1.

If you satisfy this paragraph then R3 could be used and yes, I would agree with your interpretation of Table 12.8-2
 
Ron,

Thanks, the SDC for this particular structure is B with a height of approx 44 feet. So I am justified in using a system with R=3.
 
The intent of the table is for the eccentrically braced frame to meet seismic detailing provisions. R=3 eccentric braced frames should use a Ct of 0.02 for an "All other structural systems." This was clarified in ASCE 7-10 where the exact same table now says "steel eccentrically braced frames in accordance with Table 12.2-1 lines B1 and D1" which are the higher R seismically detailed eccentric systems.
 