So the manufacturer of the wall ties specify whether their product is a light, medium or heavy duty based on compliance tests (I assume) which then gives a characteristic capacity as specified in the code. Let's say medium duty so it has a 400N tension and 480N compression characteristic capacity. The masonry code then says that a 0.95 reduction factor is to be applied to wall ties, giving a design strength of 380N tension and 456N compression and the ties are not to be spaced any greater than 600 x 600 centers.
For my typical situation (Region B; Importance Level 2) the ultimate wind pressure is 1.21kPa (at ground level). The greatest pressure co-efficients occur at side walls -0.65 with an local multiplier Kl of 2.0. This gives a design tension force on the wall ties of 566N. Even if I have my wall studs at 450crs which I usually do, the design tension force on the wall tie is still 424N.
Living in Brisbane, I have always called up medium duty wall ties which I now begin to think is under capacity. Does anyone who designs in Region B call up medium duty wall ties at 600crs. I have only seen one design to date which has called up heavy duty ties and that was for a carpark balustrade wall in Region B.
Also, silly question for asking, but what is the maximum span/deflection ratio for stud walls which are supporting a brick veneer wall. I have been using span/200 which allows movement of 13.5mm in the wall at midspan for a 2700 high wall.