Area Operator Cabin

Status
Not open for further replies.

ada6618

Chemical
Joined
Jul 7, 2016
Messages
3
Location
PK
Dear All,
I am working at Ammonia plant,
During Hazop review, qustion arises requirment of area operator cabin electrical appliances classification. Area operator cabin are outside the classified area around 10 meters away.
NFPA define any requirements for electrical appliances installation in operator cabin?
Any reference from other ammonia plants operators.

Adnan
 
Review National Electrical Code Article 500 for hazardous (classified) location requirements. Also, review NFPA 497 which is the Recommended Practice for the Classification of Flammable Liquids, Gases, or Vapors and of Hazardous (Classified) Locations for Electrical Installations in Chemical Process Areas.
 