byrnesf: You excluded some VERY important words with your post.........."Where supervised automatic sprinkler systems are required by another section of this Code,". {This is the primary point I attempted to address with my quick and short post.}
NFPA 1 (Uniform Fire Code 2006) & NFPA 101 (Life Safety Code 2006) both state the following:
13.3.1.7 Supervision.
13.3.1.7.1* Supervisory Signals. Where supervised automatic sprinkler systems are required by another section of this Code, supervisory attachments shall be installed and monitored for integrity in accordance with NFPA 72, and a distinctive supervisory signal shall be provided to indicate a condition that would impair the satisfactory operation of the sprinkler system. System components and parameters that shall be monitored shall include, but shall not be limited to, control valves, fire pump power supplies and running conditions, water tank levels and temperatures, tank pressure, and air pressure on dry-pipe valves. Supervisory signals shall sound and shall be displayed either at a location within the protected building that is constantly attended by qualified personnel or at an approved, remotely located receiving facility. [NFPA 101:9.7.2.1]
Read Sections 13.3 through 13.3.2.27 of NFPA 1 and/or Sections 11 through 42 of NFPA 101. There are several common occupancies which do not require "supervised" automatic sprinkler systems; therefore, no tamper switches and other monitored electronic devices are required. Some of the common examples would be Mercantile Class B, warehouse storage buildings, existing apartment buildings up to 4 stories (with limitations), as well as lodging & rooming houses among several other occupancies.
NFPA 101 also indicates the following:
4.6.8 Provisions in Excess of Code Requirements. Nothing in this Code shall be construed to prohibit a better type of building construction, an additional means of egress, or an otherwise safer condition than that specified by the minimum requirements of this Code.
Personally, I would prefer that all fire protection system components were electronically supervised; however, the current NFPA documents do not require this level of monitoring/reliability for all occupancies/risks.
I should clarify that my 16 Nov 10 post was unclear/incorrect when I stated "The valves associated with the combined Backflow Prevention Unit (fire & domestic service) are not part of the "dedicated" fire protection system. Therefore, the tamper switches are not required in this instance." I missed the fact that SD2 stated this is a large Mall.......my comments would be correct for a system designed using NFPA 13R or NFPA 13D, but incorrect for any NFPA 13 system which requires "supervised" alarms. A large Mall is considered Mercantile Class A which requires a "supervised" automatic sprinkler system throughout all areas so the tamper switches should be provided for the two valves on the backflow prevention unit (essentially any control valve on the Mall property which would prevent water flow to any of the automatic sprinkler systems in the Mall buildings when fully closed should be electronically supervised!).
I apologize for posting an incorrect statement and for any confusion I caused. We all make mistakes......at least my intentions were good.