thejonster
Structural
- Feb 8, 2011
- 69
Column strip middle strip assumptions concentrate moments & shears in ultimate, and stresses in service for mild 2 way slab design.. should this also apply in prestressed/ Post-tensioned design?
I was very interested in ACI 318-14 researching this question because the re-organization put mild and prestressed 2 way slabs in the same section.
I found in ACI 318-14 8.4.1.2 that prestressed 2 way slabs shall be designed by the equivalent frame method, and R8.11.2 that the equivalent frame consists of 3 parts: column, joint, and slab beam strip. The slab beam strip is shown as 'full width' or same width as the tributary area for loading. Same as ACI 318-11
the equivalent frame section of 318-14 (8.11) has no guidance for concentrating the moment or stresses in the column strip, and the direct design section where those forces and stresses are concentrated is prohibited for prestressed design.
RAM Concept support has a page online: Frequently Asked Questions
When should design strips be modeled with column and ½-middle strips and when should they be modeled as full-width column strips? They advocate that col & mid strips be modeled, concentrating the moment and stresses to the col strip.
I spoke with an Adapt designer who says that 95% of 2 way slab designers model as 'full width', and he pointed out that ACI 318-11 chapter 18 says ch 13 does not apply, and he pointed out that the equivalent frame has nothing to do with col strip mid strip, but rather the vertical frame including columns floor to floor.
Applying csms assumptions will make the design much harder and less economically competitive vs soil treatment under a basement. There is no life safety risk in our particular application as this is a residential basement floor on pier supports.
I have primary experience in 1 way garage pt slabs and limited experience in 2 way design.
Edit:
This is for a 2 way flat plate design
I was very interested in ACI 318-14 researching this question because the re-organization put mild and prestressed 2 way slabs in the same section.
I found in ACI 318-14 8.4.1.2 that prestressed 2 way slabs shall be designed by the equivalent frame method, and R8.11.2 that the equivalent frame consists of 3 parts: column, joint, and slab beam strip. The slab beam strip is shown as 'full width' or same width as the tributary area for loading. Same as ACI 318-11
the equivalent frame section of 318-14 (8.11) has no guidance for concentrating the moment or stresses in the column strip, and the direct design section where those forces and stresses are concentrated is prohibited for prestressed design.
RAM Concept support has a page online: Frequently Asked Questions
When should design strips be modeled with column and ½-middle strips and when should they be modeled as full-width column strips? They advocate that col & mid strips be modeled, concentrating the moment and stresses to the col strip.
I spoke with an Adapt designer who says that 95% of 2 way slab designers model as 'full width', and he pointed out that ACI 318-11 chapter 18 says ch 13 does not apply, and he pointed out that the equivalent frame has nothing to do with col strip mid strip, but rather the vertical frame including columns floor to floor.
Applying csms assumptions will make the design much harder and less economically competitive vs soil treatment under a basement. There is no life safety risk in our particular application as this is a residential basement floor on pier supports.
I have primary experience in 1 way garage pt slabs and limited experience in 2 way design.
Edit:
This is for a 2 way flat plate design