Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Arc Flash (NFPA 70E)

Status
Not open for further replies.

wbd

Electrical
Joined
May 17, 2001
Messages
659
Location
US
Hello,
I'm looking for some information on what other companies are doing in the area of NFPA 70E, specifically in the area of arc flash hazards.

1. Have you done a arc flash hazard analysis using calculations?
2. If not, are you using the tables in NFPA 70E for the PPE requirements?
3. If you are a US utility, what are you using for a guide in selecting PPE for arc flash?

Thank You
 
wbd,

We've done several arc-flash studies based on calculations for a variety of industrial facilities. We are presently doing studies for some large fossil-fuel power plants for a US utility.

All of our calculations have been based on IEEE-1584 equations.

Outdoor substations are another matter. I know some large industrials who have done studies for their substations. I'm not aware of any utilities who have addressed arc-flash in outdoor subs, although I'm sure they must be thinking about it. I have had some discussions with utility engineers regarding arc-resistant metalclad switchgear and bus differential to reduce arc-flash hazards.

Hope that helps.

 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top