Thanks guys,
What do you guys think of my approach as follows:
Section 5.10.4.4 of API 650 provides calculation on rafter spacing. Is it acceptable for me to work backwards if I know the maximum roof plate span (6.5' in my case), Fy being 30,000psi, and the corroded roof thickness, and try to calculate the uniform pressure p from the equation.
From this p, I can work on the load combinations from section 5.2.2, whichever case with the maximum psf, I subtract that maximum number by the p I got from the rafter equation, and the remaining difference is the psf that the roof plate can still handle (I can convert the nozzle load into psf based on the area of the nozzle). Then I will calculate the load acting on the area of the nozzle with the self weight of the nozzle, as well as the additional appurtenance that is being attached to that nozzle. Compare the two numbers at the end.
Does this approach seem reasonable by any means?