Jul 16, 2012 #1 MACARTHUR Petroleum Joined Apr 20, 2009 Messages 6 Location FR thread184-219005 Could someone tell me whether the API65011th Edition repeats the NFPA11 the exact wordings for foam dams design? And at which parag. / Annex? Thanks
thread184-219005 Could someone tell me whether the API65011th Edition repeats the NFPA11 the exact wordings for foam dams design? And at which parag. / Annex? Thanks
Jul 19, 2012 #2 IFRs Petroleum Joined Nov 22, 2002 Messages 4,682 Location US For external floating roofs it is in C.3.15.2 For internal floating roofs it is H.5.9 Both refer to NFPA 11 and if you are in compliance with NFPA 11 you will be in compliance with API 650. Upvote 0 Downvote
For external floating roofs it is in C.3.15.2 For internal floating roofs it is H.5.9 Both refer to NFPA 11 and if you are in compliance with NFPA 11 you will be in compliance with API 650.