Mondolfi
Chemical
- Aug 12, 2003
- 22
For safety devices the overpressures indicated as 20% and 10% above maximum allowable working pressure apply to API 620 tanks only. As indicated in 4.5.1.1.4, these conditions do not apply to API 650 tanks where the internal design pressure should not be exceeded under any normal operating condition.
I understand that "Fire" wouldn't be a "normal operation condition". There for, if the tank is API650 can I assume an overpressure (let's say 10%) above the MAWP of the tank (in my case design pressure) or shall I fix the set point to a lower figure so I never pass the MAWP?
Best regards,
I understand that "Fire" wouldn't be a "normal operation condition". There for, if the tank is API650 can I assume an overpressure (let's say 10%) above the MAWP of the tank (in my case design pressure) or shall I fix the set point to a lower figure so I never pass the MAWP?
Best regards,