I am providing the design and foundation details for a Vietnam Memorial wall for the City I live in in Southern California.(high seismic zone)
This is a 5300Lb granite wall with two 1.25" dia holes placed in the bottom for anchorage. See attached sketch.
I am designing this per ASCE 7-16 section 15 under non bldg structures not similar to buildings. I am using an R value of 1.25 and since the Sds is 1.036 the resultant seismic rxn is pretty large.
My concern is that the two holes that are provided for anchorage would crack the granite wall in the event of the design seismic event. Actually since I am using load combinations per 2.4.5 my DL is reduced to 0.45D and with the uplift force at each A.B. of 10.5kips I do not see a way to anchor this wall section.
Any comments or thoughts would be highly appreciated.
Thanks
This is a 5300Lb granite wall with two 1.25" dia holes placed in the bottom for anchorage. See attached sketch.
I am designing this per ASCE 7-16 section 15 under non bldg structures not similar to buildings. I am using an R value of 1.25 and since the Sds is 1.036 the resultant seismic rxn is pretty large.
My concern is that the two holes that are provided for anchorage would crack the granite wall in the event of the design seismic event. Actually since I am using load combinations per 2.4.5 my DL is reduced to 0.45D and with the uplift force at each A.B. of 10.5kips I do not see a way to anchor this wall section.
Any comments or thoughts would be highly appreciated.