Anchor rod mislocated - edge distance issue

Status
Not open for further replies.

structSU10

Structural
Mar 3, 2011
1,062
Are there any official publications, recognized per code, that allow for less than the minimum edge distance for an anchor rod in a steel baseplate while providing a welded oversized washer? Assuming all other issue are resolved, what are opinions on oversized washers 'extending' the edge distance?
 
Replies continue below

Recommended for you

Can give a little more information? What kinds of forces are you resisting?

If it's the baseplate for a steel column subjected to nothing other than a downward gravity load then is there a minimum edge distance??
 
Reference 3rd Quarter 1989 AISC Engineering Journal Article by David T. Ricker "Some Practical Aspects of Column Base Selection".
 