Analysis of OWSJ truss for HVAC point load

Status
Not open for further replies.

jt0716

Structural
Joined
Dec 6, 2010
Messages
11
Location
US
I'm having issues determining my limiting forces on an existing truss. I've determined that the truss is a 24LH05. I've also figured that under distributed loading of snow and dead loads, i'm within the allowable limits. In addition, if i convert the point load to a distributed load, i'm within allowable limits, however, i know the nature of the truss doesnt necessarily work that way. I'm trying to certify whether a roof-mounted HVAC unit (800#) can span two adjacent trusses (6.5' spacing) without compromising the truss. I can solve for joint forces, but i cant figure out how to determine my limiting factors due to point loads. I appreciate further advice..
 
Take a look at these two previous threads:

thread507-134172

thread507-127992
 
Don't forget to consider snow drift resulting from the roof projection. That is often the determining factor. It would be a rare case where two joists designed for a uniform snow load are capable of carrying an 800# mechanical unit without modification.