SprinklerDesigner2
Mechanical
I got a little job where the ceiling is 16'-6" and FM Global directed me to FM Data Sheet 8-9 Table 8
I know I am reading this correctly but the pressures seem awfully low to me.
Using K25.2 EC https://www.vikinggroupinc.com/sites/default/files/2025-03/121610.pdf all I need is 6 heads discharging at 22 psi with spacing up to 14'x14'?
Or 12 K16.8 ESFR pendent sprinklers at 13 psi?
I know that is the correct answers but the pressures just seem awfully low for a building with a peak at 26'-6".
I know I am reading this correctly but the pressures seem awfully low to me.
Using K25.2 EC https://www.vikinggroupinc.com/sites/default/files/2025-03/121610.pdf all I need is 6 heads discharging at 22 psi with spacing up to 14'x14'?
Or 12 K16.8 ESFR pendent sprinklers at 13 psi?
I know that is the correct answers but the pressures just seem awfully low for a building with a peak at 26'-6".