Sep 5, 2003 #1 egc Structural Joined Oct 11, 2002 Messages 38 Location MX If you use ACI 318-02 14.8 to design the reinforcing for a wall, do the maximum spacing restrictions sited in 14.3.5 apply? I just hang here (occasionally)
If you use ACI 318-02 14.8 to design the reinforcing for a wall, do the maximum spacing restrictions sited in 14.3.5 apply? I just hang here (occasionally)
Sep 11, 2003 #2 JAE Structural Joined Jun 27, 2000 Messages 15,715 Location US I would say yes, 14.3 applies. 14.8 is an alternative to 10.10 (column design) and does not exclude 14.3 directly. Upvote 0 Downvote
I would say yes, 14.3 applies. 14.8 is an alternative to 10.10 (column design) and does not exclude 14.3 directly.