I have designed an elevated platform on top of a building. As per ASCE, I used L/360 as deflection limit for all the beams in my design. Do we have to use the same factor for columns? My platform design is governed by Wind Load.

Thanks
 
Replies continue below

Recommended for you

Deflection control is a purely serviceability issue - not a code/strength issue.

Since this sounds like a pure steel platform out in the air, the only deflection control is what you might see appropriate for human comfort walking on it.

Without a full blow vibration analysis or something like that - your use of L/360 for vertical LL deflection would be OK.

For lateral sway - for structures like this - I'd probably lean also to L/360 or L/400.

Check out Eng-Tips Forum's Policies here:
faq731-376
 
L/360 for the columns (for wind) is possibly tighter than you need, unless you have finishes to protect (etc.). Not a bad starting point though.

----
just call me Lo.
 
I typically use a wind speed based on a lesser mean recurrence interval (MRI), say 10-year or 25-year MRI, for lateral deflection (drift) computations. Wind speed charts for various mean recurrence intervals are provided in the Commentary to ASCE 7-10 Appendix C. You should, of course, evaluate the sensitivity to movement of the equipment supported by the platform. With the reduced wind pressure, I would then aim for a drift limit in the H/300 to H/400 range, provided the equipment or your client have not imposed a more strict limit.
 