DavyBeans
Structural
- Feb 8, 2011
- 3
I'm currently working on a job in London involving putting some temporary needles thru a 400mm thick masonry wall. The load on the wall at the temporary needling level is approx 200kN/m.
In the permanent sense building control will allow an allowable compressive force of 0.63N/mm2 under a concentrated load for an existing masonry Wall as per Ciria Report 111.
Is anybody aware of what the allowable compressive force is for masonry bearing on top of a temporary needle? There is no indication of same on any of the current codes available to me.
For a 203UC needle my allowable compressive force will only be (Fc / 203mm x 400mm) = 0.63N/mm2. Fc = 51kN with needles spaced at 1.0m ctrs. My needles would need to be spaced at 255mm ctrs to comply with this rule.
Is a relaxation of this compressive force allowable in the temporary sense? Or is anyone aware of a code which might give suitable guidance for masonry compressive forces on tempoary needles?
Thanks in advance.
In the permanent sense building control will allow an allowable compressive force of 0.63N/mm2 under a concentrated load for an existing masonry Wall as per Ciria Report 111.
Is anybody aware of what the allowable compressive force is for masonry bearing on top of a temporary needle? There is no indication of same on any of the current codes available to me.
For a 203UC needle my allowable compressive force will only be (Fc / 203mm x 400mm) = 0.63N/mm2. Fc = 51kN with needles spaced at 1.0m ctrs. My needles would need to be spaced at 255mm ctrs to comply with this rule.
Is a relaxation of this compressive force allowable in the temporary sense? Or is anyone aware of a code which might give suitable guidance for masonry compressive forces on tempoary needles?
Thanks in advance.