- Feb 22, 2005
- 93
We have a job in the office where we are working for the steel fabricator to design the moment connections for a project. The EOR has asked that all moment connections be designed for full moment strength of each beam.
The moment connections are directly welded (DW) moment connections. Beam flanges are field welded to column flanges with CJP welds. Rat holes and backer bars are used. Shear is taken care of by a single plate connection.
My question is: Is it possible for this type of connection to be strong enough using the 2005 AISC specification?
It used to be we didn't check anything with regard to the weld if it was CJP. Now the specification includes equations; J2-2 and J2-3. It specifically ask for the base metal to be checked. Although when you go to table 2.5 for the omega factor (we are using ASD), there are no values given under CJP welds, it just says strength is controlled by base metal.
Since there is a rat hole next to the beam flange. I suppose I have to check the flange as a plate for tension yielding.
Here is an example of what I'm running into:
Beam: W18x46
Maximum Moment: 226 k-ft
d = 18.1 in
tf = 0.605 in
bf = 6.06 in
Flange force = 226*12/(18.1-0.605) = 155.02 kip
Tension Yielding of Flange = 0.605*6.06*50/1.67 = 109.77 kip
109.77<155.02 N.G.
Is this going to be the case for every beam? Is it impossible to develop the full moment capacity of a beam with this type of connection?
The moment connections are directly welded (DW) moment connections. Beam flanges are field welded to column flanges with CJP welds. Rat holes and backer bars are used. Shear is taken care of by a single plate connection.
My question is: Is it possible for this type of connection to be strong enough using the 2005 AISC specification?
It used to be we didn't check anything with regard to the weld if it was CJP. Now the specification includes equations; J2-2 and J2-3. It specifically ask for the base metal to be checked. Although when you go to table 2.5 for the omega factor (we are using ASD), there are no values given under CJP welds, it just says strength is controlled by base metal.
Since there is a rat hole next to the beam flange. I suppose I have to check the flange as a plate for tension yielding.
Here is an example of what I'm running into:
Beam: W18x46
Maximum Moment: 226 k-ft
d = 18.1 in
tf = 0.605 in
bf = 6.06 in
Flange force = 226*12/(18.1-0.605) = 155.02 kip
Tension Yielding of Flange = 0.605*6.06*50/1.67 = 109.77 kip
109.77<155.02 N.G.
Is this going to be the case for every beam? Is it impossible to develop the full moment capacity of a beam with this type of connection?