platypus83
Mechanical
- Nov 14, 2008
- 10
i have a question about delta t for heating coils in fan coil units
it seems like a stupid question but anyway
if a heating system is designed as 82deg c flow and 71 deg c return therefore an 11 deg c delta t. If all the coils in the system are also designed for 11 deg delta t at design flow rate of water. Assuming that heating water flows and airflows across coils are at design, what would the effect of running the boiler at 70 deg c be?
would the return water temp be 11 deg c lower? (i.e. 69 deg c)
would the air still achieve its design heat gain across the coil? assuming max air temp design is 24 deg c
basically what im wondering is how important is the flow temp of the water?
i know in design Q = mc delta t is used for boiler size, coil sizes, airflow and water flowrates but that only uses a delta t and not an actual temp.
it seems like a stupid question but anyway
if a heating system is designed as 82deg c flow and 71 deg c return therefore an 11 deg c delta t. If all the coils in the system are also designed for 11 deg delta t at design flow rate of water. Assuming that heating water flows and airflows across coils are at design, what would the effect of running the boiler at 70 deg c be?
would the return water temp be 11 deg c lower? (i.e. 69 deg c)
would the air still achieve its design heat gain across the coil? assuming max air temp design is 24 deg c
basically what im wondering is how important is the flow temp of the water?
i know in design Q = mc delta t is used for boiler size, coil sizes, airflow and water flowrates but that only uses a delta t and not an actual temp.