I am looking for any web links that detail method for calculating indoor air exchange rates.
Any links to recommended limits for industrial plants are also appreciated.
 
Replies continue below

Recommended for you

Air exchange rate (ACH) is just:

(cfm * 60) / room volume in ft3

ACH requirements would typically be based on generation rate of fugitive emissions for a plant. That could vary a bit...
 
You also have to clarify which cfm to use. It could be: supply air to get SA ACPH (air change per hour);
OA to get OA ACPH; or room total air which is the sum of supply air + transfer air in or sum of exhaust air + transfer air in. Note that in a room SA + TA in = Exh + TA out.
 
daewoo
From other posts that you have placed, apparently your facility deals with anodized Aluminum in a machine shop environment.
As ChasBean1 and lilliput1 indicate air change rates
for an industrial facility could have a wide variation.
The air change rate would be determined by specific codes,
or could be the result of dealing with a heat load,
or could be the sum of exhaust ventilation associated with each process, if your facility is not conditioned and only ventilated, and heated with make-up air.
When you say indoor air exchange rates, that indicates
return air only. Can you provide more information ?
 