Back to basics here, I've got a pump on a VFD running at 60 Hz. It's moving 550 gpm with 90 ft. of head. If I slow this pump down until it moves only half the water, or 275 gpm, what will its head be? Thanks.
Or
Pump affinity for centrifugal pumps with no change in pump diameter
Flow prop to speed
head prop speed^2
power prop ^3
So half the speed, a quarter of the head so 90/4 = 22.5 ft
whether this works or not will depend clearly on your static head and system curve.
If it's not moving any (or less) water at half the speed the head will be higher up the curve....