I'm working on a screen for seperating different sizes of rocks. The original motor was an old GE U frame 10 horse design B. It was replaced with a Baldor NEMA Premium design A 10hp motor. Since it was replaced there has been a problem getting the motor to start. The FLA is 12.5 @ 480v. The motor pulls about 90A for 20s before it settles down to about 8A. From what I've read about design A motors this is a common problem, and is usually solved by using a soft start.
From what I've heard the old U frame motors had alot more starting torque then modern motors. I'm wondering if I should try a design C or just stick with a B. Are there disadvantages in using a C? I know that there is more slip allowed, and I will be using a Premium efficiency motor.
The A has to go. We are having to run bigger overloads in order to get it to start, and also some of the wiring from the starter to the overloads showed signs of severe heat damage, and had to be replaced.
From what I've heard the old U frame motors had alot more starting torque then modern motors. I'm wondering if I should try a design C or just stick with a B. Are there disadvantages in using a C? I know that there is more slip allowed, and I will be using a Premium efficiency motor.
The A has to go. We are having to run bigger overloads in order to get it to start, and also some of the wiring from the starter to the overloads showed signs of severe heat damage, and had to be replaced.