I'm really surprised to not find this topic in the eng-tips archive, but perhaps my google foo is lacking.
This is a super basic question that I'm sure comes up all the time, but I would like to know what your general approach is.
I have an existing two story wood framed structure with an exterior plywood wall. The client would like to penetrate this wall with a new window.
I propose to assume this wall is a shear wall, calculate the required wind/seismic shear load capacity, and then design the wall, as if it were new, using the "force transfer around opening" method. providing blocking and strapping above and below the window as required.
This would presumably avoid the need to add holdowns at the king studs.
The problem I can forsee is assuming the shear capacity of the existing ply on the "piers" to the left and right of the proposed window. It seems that no matter what I did, the shear demand on these piers would be increased. Assuming I'm unable to determine the sheathing and nailing before hand, what should I use as an allowable shear value? Clearly anything under 100 plf [ASD] would be OK, but if it were 250plf [ASD], what would you do?
Attached is a typ detail I plan to use for inspiration.
This is a super basic question that I'm sure comes up all the time, but I would like to know what your general approach is.
I have an existing two story wood framed structure with an exterior plywood wall. The client would like to penetrate this wall with a new window.
I propose to assume this wall is a shear wall, calculate the required wind/seismic shear load capacity, and then design the wall, as if it were new, using the "force transfer around opening" method. providing blocking and strapping above and below the window as required.
This would presumably avoid the need to add holdowns at the king studs.
The problem I can forsee is assuming the shear capacity of the existing ply on the "piers" to the left and right of the proposed window. It seems that no matter what I did, the shear demand on these piers would be increased. Assuming I'm unable to determine the sheathing and nailing before hand, what should I use as an allowable shear value? Clearly anything under 100 plf [ASD] would be OK, but if it were 250plf [ASD], what would you do?
Attached is a typ detail I plan to use for inspiration.