Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

adapters

Status
Not open for further replies.

Lc85

Electrical
Apr 14, 2011
107
Can you get an adapter for a 3 pin Hirschmann type plug to allow 3/4" NPT conduit to be fitted on a solenoid valve?

Thanks
 
Replies continue below

Recommended for you

You can definitely get NPT adapters for the MIL-C-5015 series although it is a little larger than the smaller Hirschmann connectors.

I haven't seen NPT adapters for the Hirschmann stuff but NPT isn't so common over in Europe on electrical fittings. You can likely get one manufactured fairly easily though by any half-decent jobbing machine shop.

BTW, have you looked at Lemo as an alternative to Hirschmann - very similar in price, quality, etc. Both are very good.
 
This plug is on a solenoid valve, is their any other way that would allow 3/4" NPT to be fitted?
Thanks
 
3/4" NPT is a massive entry for a solenoid valve. If the entry is about 2/4" diameter then it's probably 1/2" NPT.

Are you tied to Hirschmann? Which series of connector? The commercialised military types I referenced above are fairly popular for things like solenoids, servo-valves and the like in power generation, steel, those sort of environments. Not much use for hazardous areas, but excellent otherwise. You might find the beautifully-engineered Hirschmann or Lemo type connectors don't like the rough & tumble in an industrial facility, if that's where your valve is located.
 
"If the entry is about 2/4" diameter then it's probably 1/2" NPT."

If the entry is about 3/4" diameter then it's probably 1/2" NPT. Wish we had an edit function!

 
Status
Not open for further replies.

Part and Inventory Search

Sponsor