ACI Cl. No: 10.6.7 - skin reinforcement for deep beam

Status
Not open for further replies.

Murali27

Structural
Sep 28, 2002
147
As per this the area of skin reinforcement on each face per foot of height shall be greater than or equal to 0.012(d-30).

In the same clause at the last sentence, it says that the total area of longitudinal skin reinforcement in both faces need not exceed the one-half of the required flexural tension reinforcement.

in our one of the example

deep beam size 8" x 144 " with the given uniform loading
requires
a. Flexural reinforcement - 4 sq.in
b. Skin reinforcement - 1.326 sq.in/ft on each face. as per the clause total area of skin reinforcement requires at spacing of 12" - 15.912 sq.in

calc:

on each face - 1.326 sq.in / ft
should be places d/2 distance from the flexural reinforcement - i.e 140.5/2 = 70.25 in
spacing should be lesser of d/6 or 12"
so on each face - 6 no of bars required so say 6*1.326 = 7.956 sq.in
so totally on the both faces - 2* 7.956 = 15.912


But as per the last sentence skin reinforcement need not be more than 2 sq.in (1/2*4 sq.in)

Please clarify on this point and your input always be appreciated.




 