archeng59
Structural
- Aug 24, 2005
- 620
Working on a project where we have steel embed plates with headed studs welded to the plates. The embed plates are installed in concrete columns. The capacity of the embed plates are controlled by side blowout because the headed studs are too close to the sides of the column. ACI 318 is vague regarding the use of supplementary reinforcing. My question is this: without supplementary reinforcing, I need to increase the column width so side blowout is not an issue or add supplmentary reinforcing through the shear cone of each stud near the edge. The architect says no-go on the column size increase. So, if I add reinforcing through the shear cone, it appears to me that side blowout can be ignored. Is that how anyone else interprets the use of supplementary reinforcing? I have vertical bars at each corner of the column and each face. Those bars pass through the side blowout zone. I will add more column ties in the area of the embed plate. Just not certain that is enough to satisfy the side blowout issue and get a larger capacity for the embed plates.