I have used CALTRANS spec:
15?2.05A Frames, Covers, Grates, and Manholes
? When existing manholes or inlets are to be abandoned, pipes entering the manhole or inlet shall be securely closed by a tight fitting plug or wall of minor concrete not less than 150-mm {0.5-foot} thick, or by a tight brick wall not less than 200-mm {0.67-foot} thick with cement mortar joints. Minor concrete shall conform to the provisions in Section 90-10, "Minor Concrete." The bases of manholes or inlets shall be broken in a manner to prevent entrapment of water. The manhole or inlet shall be demolished to an elevation one meter {3.5 feet} below finished grade and backfilled in conformance with the provisions in Section 19-3.06, "Structure Backfill."
Good luck