OK, I know that there have been many similar threads, but I still do not think they answer my questions...
I need to design a foundation for a water tank with the following info:
Volume = 8000 gal
Height = 20 ft
Diameter = 9 ft
Flat bottomed tank w/ 6 anchors
Soil bearing capacity = 2000 psf
Design snow load = 69 psf
Live roof load = 20 psf
Basic wind speed 70 mph
Seismic zone 2A
Extreme frost penetration = 60"
Well, here are my questions:
1. Since this is an anchored tank, I would assume a ring wall type footing would be the solution?
2. AWWA D100-96 states that the minimum footing depth should equal the frost penetration level. But this gives a 6'-6" high footing??? So do I then need to go with piles instead?
3. I have used the procedures in API 650 to determine the wind and seismic overturning moments. So now I have overturning moments based on either wind or seismic forces, and gravity forces based on dead, live, and/or snow loads. But how do I size the footing based on this?
Neither AWWA D100-96, nor API 650 goes into detail when it comes to the actual footing design.
I guess I can "unfold" the circular footing and treat it as a continuous footing. But how do I distribute the longitudinal forces (tension(uplift) and compression) due to the moments along the linear footing?
4. In a previous thread, an equation (from Gaylord, et.al.) for the reinforcement required to resist the lateral earth pressure due to the surcharge was provided, so I think I have that covered. Unless there are other methodologies?
Thanks,
cmhski
I need to design a foundation for a water tank with the following info:
Volume = 8000 gal
Height = 20 ft
Diameter = 9 ft
Flat bottomed tank w/ 6 anchors
Soil bearing capacity = 2000 psf
Design snow load = 69 psf
Live roof load = 20 psf
Basic wind speed 70 mph
Seismic zone 2A
Extreme frost penetration = 60"
Well, here are my questions:
1. Since this is an anchored tank, I would assume a ring wall type footing would be the solution?
2. AWWA D100-96 states that the minimum footing depth should equal the frost penetration level. But this gives a 6'-6" high footing??? So do I then need to go with piles instead?
3. I have used the procedures in API 650 to determine the wind and seismic overturning moments. So now I have overturning moments based on either wind or seismic forces, and gravity forces based on dead, live, and/or snow loads. But how do I size the footing based on this?
Neither AWWA D100-96, nor API 650 goes into detail when it comes to the actual footing design.
I guess I can "unfold" the circular footing and treat it as a continuous footing. But how do I distribute the longitudinal forces (tension(uplift) and compression) due to the moments along the linear footing?
4. In a previous thread, an equation (from Gaylord, et.al.) for the reinforcement required to resist the lateral earth pressure due to the surcharge was provided, so I think I have that covered. Unless there are other methodologies?
Thanks,
cmhski