mcarewm
Mechanical
- Apr 30, 2008
- 13
NFPA 13 8.6.5.2.1.5 . Permits heads to be spaced on opposite sides of Obstructions so long as the obstruction is not over 4'-0" .
My question is - This only applies to obstructions not more than 18" below ceiling . So if I can not meet the requirments of Tables 8.6.5.1.2 , 8.6.5.1.2(a) & 8.6.5.1.2(b) and the obstruction is lets say 20" below , I would be required to put a head in it/under it .
I just discussed this with fellow designer in my office and we both see it differently . I think we need a head he thinks as long as we are not over spaced from the center of the obstruction we don't need a head .
cheers .