I have a vacuum system with a 75 HP pump running on 480 with a SF of 1.15. FLA is 86.
The motor is running overloaded at/above the service factor load (~99-100+). We had a contractor look at the pump and give us three recommendations:
Rewind the motor to a 1.25 SF
Buy a new motor with a 1.25 SF
Buy a 100 HP motor to handle the load
We have had the motor fail many times and recent testing resulted having the largest difference in resistance between T leads be about 0.72% (readings in mOhms: 83.2, 82.6, 82.8). Resistance to ground is over 200Mohms for each T lead. The motor is only a few years old and has run for 12 hours every 36 hours. Is 0.72% a big enough difference to be concerned?
I am weary about buying a new motor/rewinding a motor for a higher SF just to run it above the FLA rating. Would this cause potential problems such as the current ones?
The motor is running overloaded at/above the service factor load (~99-100+). We had a contractor look at the pump and give us three recommendations:
Rewind the motor to a 1.25 SF
Buy a new motor with a 1.25 SF
Buy a 100 HP motor to handle the load
We have had the motor fail many times and recent testing resulted having the largest difference in resistance between T leads be about 0.72% (readings in mOhms: 83.2, 82.6, 82.8). Resistance to ground is over 200Mohms for each T lead. The motor is only a few years old and has run for 12 hours every 36 hours. Is 0.72% a big enough difference to be concerned?