I,ve been consulted about repair an Induction motor of 6KV of winding flashover, the motor data as follows:
make : Schorch – Germany
Type : KR6036G-AA06 IP55 tube cooled star connection 6000 volts 146 amps 1200KW 994 RPM 50HZ insulation class F amb. Temp. 41 C bearing type sleeve
Outdoor installation.
do we need to change the intire winding or only fix it by maybe special resin.
, can any one tell the prober way to fix this proplem or direct me to good refference about this problem.
thanks
 
do we need to change the intire winding or only fix it by maybe special resin.
I think the odds are you'll need to rewind.

BUT, there are certainly times when a winding can be saved with limited local repairs, along with clean/bake and carefully-specified post-repair electrical testing (to prove the repaired winding is sound).

Send it to a good shop and ask them for their recommendation.


=====================================