peterandersen
Electrical
- Feb 29, 2008
- 3
1. Is IEEE 525 best source for insulation-resistance (megger) testing procedures & megohm ratings for 600V cables, or some other standard or book guide?
2. What is acceptable megger readings for 600V cables? 1MOhm?, 50MOhm? Does it depend on distance? Other factors?
3. Field question: megger tested 1000LF 480/277V UG feeder,THHN in EMT, got readings on 3 out of 4 conductors 600kcmil of 1GigaOhms, 4th conductor 1.6MOhms. Did again and got same result? Is 4th cable "bad"? Any other tests to prove 4th cable ok? Does superhigh Giga readings indicate questionable megger/procedure? Don't want to repull 1000LF cable, any suggestions?
2. What is acceptable megger readings for 600V cables? 1MOhm?, 50MOhm? Does it depend on distance? Other factors?
3. Field question: megger tested 1000LF 480/277V UG feeder,THHN in EMT, got readings on 3 out of 4 conductors 600kcmil of 1GigaOhms, 4th conductor 1.6MOhms. Did again and got same result? Is 4th cable "bad"? Any other tests to prove 4th cable ok? Does superhigh Giga readings indicate questionable megger/procedure? Don't want to repull 1000LF cable, any suggestions?