bill318
Electrical
- Sep 11, 2004
- 43
We have an application that requires the use of a frequency converter 480V/60Hz mains, 400V/50Hz loads. The 50Hz side must be a low distortion sine wave so a rotary phase converter is being considered.
(Scenario 1) On the 400V/50Hz load side we will have:
1) A constant 3-phase load of 10KW
2) A 10KW 3-phase device that can regenerate AC.
During regeneration, the power generated will be consumed by the constant 10KW 3-phase load and the loading of the frequency converter drops and all is well.
(Scenario 2) On the 400V/50Hz load side we will have:
1) A constant 3-phase load of 10KW
2) A 10KW single-phase device that can regenerate AC.
During regeneration we will have 10KW flowing back on a single phase pair (10KW/400V = 25A). The 3-phase load will consume 10KW 3-phase = 14.4A per phase leaving 10.6A of current flowing back towards the frequency converter on a single phase pair.
From what I have been able to find so far, most frequency converters do not like current flowing back into them as the voltage may rise causing a shut down. One solution is to load down the single phase pair so that the frequency converter always sees a load even during regeneration. To keep the distortion low a resistive load bank could be used. Burning off the excess power as heat is not desirable in this application.
Questions:
1) Does anyone know of a phase converter that can handle these two scenarios without faulting or going out of control?
2) Since it is only a single phase pair that current would be flowing backwards on, would this current be used by the phase converter to provide a portion of the shaft torque and still remain under control?
Thanks in advance for any thoughts on this.
Bill
(Scenario 1) On the 400V/50Hz load side we will have:
1) A constant 3-phase load of 10KW
2) A 10KW 3-phase device that can regenerate AC.
During regeneration, the power generated will be consumed by the constant 10KW 3-phase load and the loading of the frequency converter drops and all is well.
(Scenario 2) On the 400V/50Hz load side we will have:
1) A constant 3-phase load of 10KW
2) A 10KW single-phase device that can regenerate AC.
During regeneration we will have 10KW flowing back on a single phase pair (10KW/400V = 25A). The 3-phase load will consume 10KW 3-phase = 14.4A per phase leaving 10.6A of current flowing back towards the frequency converter on a single phase pair.
From what I have been able to find so far, most frequency converters do not like current flowing back into them as the voltage may rise causing a shut down. One solution is to load down the single phase pair so that the frequency converter always sees a load even during regeneration. To keep the distortion low a resistive load bank could be used. Burning off the excess power as heat is not desirable in this application.
Questions:
1) Does anyone know of a phase converter that can handle these two scenarios without faulting or going out of control?
2) Since it is only a single phase pair that current would be flowing backwards on, would this current be used by the phase converter to provide a portion of the shaft torque and still remain under control?
Thanks in advance for any thoughts on this.
Bill