Hello all, i've been watching forum for a while now. There are very good and interestng posts here. I finally built up the courage to ask my first question, so here it goes. I need to rewire a 50kw diesel 12 lead generator from 120/208 to 277/480. The generator is now wired as 120/208.(1&7 to L1) (2&8 to L2)
(3&9 to L3) (4,5,6,10,11,12 tied together and to neutral tap).
I believe to get 277/480 i need to rewire as follows
1 to L1)
(2 to L2) (3 to L3) (4&7 together) (5&6 together) (6&9 together)
(10,11,12 together and to neutral tap).I think i am on the right track, any suggestions?