We had a fault in an ATS last week. Upon inspection, we found that a wire in one of the cabinets had burned through and arced in a few places.
This is a 12.47 kV ATS (nominal 15 kV). The wires feeding the loads are large 15 kV rated cables. There are also smaller (#4) wires that feed the PT's. It looks like these are only rated at 5 kV.
So one of those cables was laying against the cabinet and after about a year of service, the insulation burned through.
I am being told by the manufacturer that these wires are allowed to be 5 kV rated and that the problem is faulty installation - not keeping the wires dressed so that they stay away from the frame.
I don't understand how it can possibly be acceptable to put 5 kV rated cable in a 15 kV compartment. Isn't that a code violation?