VTer
Electrical
- Dec 23, 2008
- 240
We have a client with a facility containing (3) emergency/standby generators at 2000ekW/ 2500kVA each. The gen sets are 480V and then stepped up (3-delta-wye xfmrs) to 12,470V on a common bus(paralleled) with ties for distribution. (3ph, 3W)
Due to recent expansion, the facility requires two (2) additional gen sets to be tied to the same 12,470V switchgear. These gens are already pre ordered and will have the same power capability but will produce 12,470V directly without any step-up transformers. Since I am a recent graduate (lack much needed experience) and just assisting on the job, I was wondering if there is any possible concerns that I should be aware of with this set up (advantages/ disadvantages of 480V vs. 12470V gen sets). Since the job is in the very early stage of design, I am not concerned with synchronizing equipment, relay protection and and anything external to these units. I would only like to know the advantages/ disadvantages of 480V vs 12,470V unit, and why one would be used vs. the other in this scenario?
"Throughout space there is energy. Is this energy static or kinetic! If static our hopes are in vain; if kinetic — and this we know it is, for certain — then it is a mere question of time when men will succeed in attaching their machinery to the very wheelwork of nature". – Nikola Tesla
Due to recent expansion, the facility requires two (2) additional gen sets to be tied to the same 12,470V switchgear. These gens are already pre ordered and will have the same power capability but will produce 12,470V directly without any step-up transformers. Since I am a recent graduate (lack much needed experience) and just assisting on the job, I was wondering if there is any possible concerns that I should be aware of with this set up (advantages/ disadvantages of 480V vs. 12470V gen sets). Since the job is in the very early stage of design, I am not concerned with synchronizing equipment, relay protection and and anything external to these units. I would only like to know the advantages/ disadvantages of 480V vs 12,470V unit, and why one would be used vs. the other in this scenario?
"Throughout space there is energy. Is this energy static or kinetic! If static our hopes are in vain; if kinetic — and this we know it is, for certain — then it is a mere question of time when men will succeed in attaching their machinery to the very wheelwork of nature". – Nikola Tesla