robbm
Electrical
- Nov 2, 2005
- 56
We have a system that is designed for a 480V wye system, and the customer came back stating that their power source has 1 leg grounded (ie delta). Not having dealt with this in awhile, do I just need to make sure any 3phase devices are rated for running off 480V delta?
Regarding the devices on the system - there's a pump, 3phase electric heater, and a 480-120 transformer on the system:
The pump is running off a soft start (AB SMC-3) that is stated in the manual as having an "inside delta connection" so I think I'm good sticking with that as-is - there's just a dipswitch and separate wiring instructions it seems (assuming we're using a delta-connected motor).
The heater is controlled by a SSR and its documentation mentions hooking up to delta loads, so that should be fine too.
For the transformer, as long as I 480V between the legs going to the transformer primary terminals, i should be fine, right?
I'm told the end user is looking into a 480V-D to 480V-Y transformer, to eliminate any need for us to change anything, but want to know ramifications in case they don't go that route. Thanks in advance.
Regarding the devices on the system - there's a pump, 3phase electric heater, and a 480-120 transformer on the system:
The pump is running off a soft start (AB SMC-3) that is stated in the manual as having an "inside delta connection" so I think I'm good sticking with that as-is - there's just a dipswitch and separate wiring instructions it seems (assuming we're using a delta-connected motor).
The heater is controlled by a SSR and its documentation mentions hooking up to delta loads, so that should be fine too.
For the transformer, as long as I 480V between the legs going to the transformer primary terminals, i should be fine, right?
I'm told the end user is looking into a 480V-D to 480V-Y transformer, to eliminate any need for us to change anything, but want to know ramifications in case they don't go that route. Thanks in advance.