dinkelja
Electrical
- Dec 10, 2004
- 31
We are working at a plant with 480/277V, and is distributed using 3 wires + ground. The incomming feeders are 13.2kv to a delta - wye transformer. I guess the wye secondary is grounded somewhere at the substation? Although I only see a delta-star diagram on the nameplate. Should / does the sec. neutral of a delta-wye xfmr have to be grounded (per NEC) or can it float (star)?
Okay, so each MCC / PDP has 3 incomming wires. They derive a neutral from the structure somewhere nearby - for single phase 277 lighting. Is this good practice, the phases are by no means balanced so there is current flowing there. Why wouldn't a 4th wire be fed from the substation ground bus? Again, I am assuming that the Wye of the transformer is grounded.
My main issue is the MCC's have mostly 3 phase 460V motors. The engineers' plan to feed a 460/230V delta/delta transformer from the MCC, to run some small 1/3hp 230V motors. (We are in the US by the way.) It would be nice to have all 460V motors, chances are those motors are 230/460V rated anyways, but we can't be sure. There were also 3hp 400V motors included in the project. The engineer was going to demand the 400V motors be swapped for 460's. Why delta/delta anyways?
Lead me in the correct direction if you would. My thought was to get a 460/230V delta-wye transformer. The 460V and 230V motors should be connected wye (star), and the 400V motor in Delta. I thought that if the engineers 460/230 delta/delta was used it would yield 230V delta (of course) and 132V wye. I pointed this out what, what I thought would be the case, the response I received was all motors are connected as wye's.
Last thing, though these are small motors, is the real purpose of a 400V motor (in the US) so it can be wye/star started? BTW, I've been searching through all the old posts, lots of good info, just haven't had time to digest it all.
Jared
Okay, so each MCC / PDP has 3 incomming wires. They derive a neutral from the structure somewhere nearby - for single phase 277 lighting. Is this good practice, the phases are by no means balanced so there is current flowing there. Why wouldn't a 4th wire be fed from the substation ground bus? Again, I am assuming that the Wye of the transformer is grounded.
My main issue is the MCC's have mostly 3 phase 460V motors. The engineers' plan to feed a 460/230V delta/delta transformer from the MCC, to run some small 1/3hp 230V motors. (We are in the US by the way.) It would be nice to have all 460V motors, chances are those motors are 230/460V rated anyways, but we can't be sure. There were also 3hp 400V motors included in the project. The engineer was going to demand the 400V motors be swapped for 460's. Why delta/delta anyways?
Lead me in the correct direction if you would. My thought was to get a 460/230V delta-wye transformer. The 460V and 230V motors should be connected wye (star), and the 400V motor in Delta. I thought that if the engineers 460/230 delta/delta was used it would yield 230V delta (of course) and 132V wye. I pointed this out what, what I thought would be the case, the response I received was all motors are connected as wye's.
Last thing, though these are small motors, is the real purpose of a 400V motor (in the US) so it can be wye/star started? BTW, I've been searching through all the old posts, lots of good info, just haven't had time to digest it all.
Jared