Mar 17, 2014 #1 anildevika1991 Electrical Joined Mar 17, 2014 Messages 1 what will be the outcome if a 380 V 60 Hz Motor is connected to a 400/415V 50Hz supply
Mar 17, 2014 #2 davidbeach Electrical Joined Mar 13, 2003 Messages 9,551 Location US Read faq237-1224, it won't be good. Voltage needs to go down when the frequency goes down, not the other way around. Upvote 0 Downvote
Read faq237-1224, it won't be good. Voltage needs to go down when the frequency goes down, not the other way around.
Mar 17, 2014 Moderator #3 waross Electrical Joined Jan 7, 2006 Messages 28,794 Location CA Given the rarity of 380 Volt motors at 60 Hz, is this a hypothetical homework problem? Bill -------------------- "Why not the best?" Jimmy Carter Upvote 0 Downvote