Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

3750 Series Brooks Flow Transmitters

Status
Not open for further replies.

CaptBissell

Industrial
Jan 10, 2005
3
I don't know if anyone has encountered this problem before but here goes.
I have a 3750 Series Brooks Wafer Mag flow transmitter and the problem that I am having is this.

I have a flowhead with a K-Factor of 7638.19, I want to set a span for 20GPM. Using the formula:

(span value) * K-Factor / 60,000 = VEL

The VEL for 20GPM = 2.5460633

Using the Coil Frequency Switch Positions chart, the only CAL value I can use is 38.400 and the Switches used are 3,4,8. My problem is that when I try to use a span value that falls within the CAL= 38.400 field, I cannot get a span signal with switches 3,4,8 on. The signal stays at 4.0 ma. I have found that using any other switches settings in the chart will give me a span side output. I have found this to be the case with every 3750 Series Flow Transmitter I have tried that particular setup on. Does anyone know why? Is it in the transmitter or am I doing something wrong? Any help will be greatly appreciated.

Thank You.

P.S. Would anyone know where I can find the software needed to comunicate with a Toshiba G3 Drive Inverter
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor