Anyone have any experience with using cable bus for 35kV applications with short distances?
I'm looking at a preliminary design which uses (6) sets of 750MCM cables installed underground to connect 75MVA transformer 34.5kV secondary to secondary switchgear. Cable distance is approximately 80' between transformer secondary and switchgear located in prefabricated control building.
We're currently in the process of revising substation layout and have an option to move control building closer to transformer. With the control building located in closer proximity to transformer I was looking into feasibility of using overhead cable bus between transformer and switchgear.
To me overhead cable bus vs underground cable presents an option for lower cost installation and easier maintenance and reliability.
I've used non-seg busduct successfully at 5kV & 15kV but from what I understand this becomes a bit more bulky and prohibitive at 35kV.
Interested to hear any pros/cons experience from others with cable bus at MV applications. Is there a maximum distance for cable bus beyond which makes its applicable not practical?
On a similar note is it typical for a yard having multiple transformers to have each transformer's secondary switchgear in a separate control building vs combined into a single control building?
I'm looking at a preliminary design which uses (6) sets of 750MCM cables installed underground to connect 75MVA transformer 34.5kV secondary to secondary switchgear. Cable distance is approximately 80' between transformer secondary and switchgear located in prefabricated control building.
We're currently in the process of revising substation layout and have an option to move control building closer to transformer. With the control building located in closer proximity to transformer I was looking into feasibility of using overhead cable bus between transformer and switchgear.
To me overhead cable bus vs underground cable presents an option for lower cost installation and easier maintenance and reliability.
I've used non-seg busduct successfully at 5kV & 15kV but from what I understand this becomes a bit more bulky and prohibitive at 35kV.
Interested to hear any pros/cons experience from others with cable bus at MV applications. Is there a maximum distance for cable bus beyond which makes its applicable not practical?
On a similar note is it typical for a yard having multiple transformers to have each transformer's secondary switchgear in a separate control building vs combined into a single control building?