Hi cyriousn, we adopt a very similar solution for our "standard" renewable energy collection substations:
we use three-windings transformers, rated at 150 kV / 36 kV / 36 kV, YNdd, with a power rating of 250/125/125 MVA, with the two MV winding connected each one to a distinct 36 kV busbar.
As prc mentioned, the short circuit rating of the breaker is also a concern. Although modern 40.5 kV class vacuum circuit breakers can easily achieve a short circuit breaking current of 31.5 kA, it's important to consider also the contribution from generators connected to each busbar. Wind turbines and innovative "grid-forming" inverters for PV systems can ,to some extent, contribute to the short circuit current.
Therefore, it may be beneficial to utilize a three-winding transformer (as also bacon4life said) to reduce the short circuit contribution from the grid-side without increasing the transfomer short circuit impedance, as a much higher short circuit impedance could compromise reactive power support from Renewable Energy Sources.
A three-winding transformer of this type is not particularly complex; indeed, compared to a two-winding machine of equal power, it presents fewer issues for short circuit withstand.