Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations TugboatEng on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

30 ft high CMU Wall

Status
Not open for further replies.

FiniteElemet

Civil/Environmental
Joined
May 16, 2004
Messages
41
Location
US
I am designing 12" CMU load bearing wall in a box building to resist 25psf wind load. Have designed at most 20 ft highs in the past so looking for design help. Any design experience will be appreciated. Building is 95ftx95ft.

Thanks,
 
Also, what can be done to increase lateral stability of wall such as providing additional bond beams!
 
A 12-inch wall should not have a problem spanning vertically at that wind load. You'll probably need two bars per cell located near each edge. I would add a single-course bond beam at 8 feet oc to help with horizontal reinforcement.
 
Thanks UcfSE,

Providing No.6@16"oc verticals near the shell gives me d=8.75". (viz. 11.625"-1"shell-1"cover-0.375=8.75". Do you agree with this d value?

Response much appreciated.
 
That d should be fine, if you're in the US using standard units. Note that a 12" block face shell is probably more like 1.25".
 
Have you considered a steel superstructure with 8" CMU's around... gets away from scheduling construction a bit and avoids a bunch of scaffolding... also a good mason can lay up about 40% more 8" block over 12" block...

Just some thoughts...

Dik
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top