HYDL
Electrical
- Feb 21, 2005
- 22
We recently installed a new Asco closed transition ATS to feed a new data center at a hospital. To test the system, the electrician shut off the utility breaker feeding the transfer switch and the generator started up and the ATS transferred to emergency power. After the test was over, the utility breaker was turned back on and after a period of time the ATS transferred back to utility using it's closed transition feature. Upon transferring, the 800 amp breaker up stream of the 225 amp breaker serving this ATS on the normal side tripped. The 225 amp breaker does not have GFP, but the 800 amp does and is on the lowest setting.
The ATS is 3-pole. The ATS Feeders are 480 volt 3-phase, 3-wire.
I am looking for ideas as to why that breaker tripped during ATS transfer. GF on the lowest setting make me think that it probably did trip on GF.
The ATS is 3-pole. The ATS Feeders are 480 volt 3-phase, 3-wire.
I am looking for ideas as to why that breaker tripped during ATS transfer. GF on the lowest setting make me think that it probably did trip on GF.