Gents,
Imagine 3 off 11kv/400V transformers feeding an LV switchboard with bus section switches between each section. All interlocked to prevent transformers operating in parallel. (2 from 3 scheme).
I say the bus section switches should be 4 pole to prevent earth fault circulating current and ensuring disconnection of the faulty circuit.
A fellow engineer insists on 3 pole and a solid neutral throughout.
Any thoughts ?