I have on site an Alsthom induction motor coupled to a sulzer HP boiler feed pump. The motor is running at 106% FLC and has been since 2006, I cannot look further back as there are no records. The plant was commissioned in 1995. Spec as follows:
2 pole 3300V 50Hz 2900kW Water at 40 deg C
2973rpm 575A 0.91pf class F insulated, White metal sleeve bearings.
The protection has been set up so that the overload curve is entered at 107% FLC. I have been told that this is working to an old CEGB standard, a rule of thumb I gather as I have seen no documents on this while trawling through old GOMs.
As the motor sometimes enters the OL curve I have been asked to further up the overload protection in order to keep the pump available. I feel uncomfortable with this as being new to the company I am unaware of this practice.
During my research I have found that the winding temperatures while stopped are 23*C. The Temperature at 107% FLC are 105-120*C.
My questions are:
As the insulation is rated F and we are well bellow the 155*C rating, are we damaging this motor by running at this increased load. By this I mean is the increased current flow in the stator likely to cause flash overs or un measurable heating affect on the rotor?
As there is no service factor, the service factor is assumed to be 1. Is there a calculation or method for calculating decrease in life expetency by exceeding the FLC continously?
I am very sorry for my limited understanding of this subject and hope that somebody could at least shove me in the right direction.
Althom sized the motor to be 15% larger than needed to drive the pump, therefore there are obviously issues with the system or pump. I do not want to put my asset at risk to nurse this problem through and distract from the real issue. I do however want to understand better the affect of running an induction machine in this way.
Thanks, T
I have searched this subject with some success but the thread I'm after is now closed.
I have on site an Alsthom induction motor coupled to a sulzer HP boiler feed pump. The motor is running at 106% FLC and has been since 2006, I cannot look further back as there are no records. The plant was commissioned in 1995. Spec as follows:
2 pole 3300V 50Hz 2900kW Water at 40 deg C
2973rpm 575A 0.91pf class F insulated, White metal sleeve bearings.
The protection has been set up so that the overload curve is entered at 107% FLC. I have been told that this is working to an old CEGB standard, a rule of thumb I gather as I have seen no documents on this while trawling through old GOMs.
As the motor sometimes enters the OL curve I have been asked to further up the overload protection in order to keep the pump available. I feel uncomfortable with this as being new to the company I am unaware of this practice.
During my research I have found that the winding temperatures while stopped are 23*C. The Temperature at 107% FLC are 105-120*C.
My questions are:
As the insulation is rated F and we are well bellow the 155*C rating, are we damaging this motor by running at this increased load. By this I mean is the increased current flow in the stator likely to cause flash overs or un measurable heating affect on the rotor?
As there is no service factor, the service factor is assumed to be 1. Is there a calculation or method for calculating decrease in life expetency by exceeding the FLC continously?
I am very sorry for my limited understanding of this subject and hope that somebody could at least shove me in the right direction.
Althom sized the motor to be 15% larger than needed to drive the pump, therefore there are obviously issues with the system or pump. I do not want to put my asset at risk to nurse this problem through and distract from the real issue. I do however want to understand better the affect of running an induction machine in this way.
Thanks, T