2010 CBC Concrete Provision relating to ACI318 Appendix D

Status
Not open for further replies.

palves

Structural
Joined
Jun 6, 2008
Messages
61
Location
US
Is anybody familiar with CBC provision 1908.1.9. It basically refers to Appendix D.3.3.4 but gives us exceptions when we don't need to follow D.3.3.4. Exception 2 applies when the anchor force is calculated using ASCE7 equation 12.11-1, which applies to Anchorage of Concrete Walls to Flexible Diaphragms.

We're retrofiting a building and my dilemma involves the connection of an existing concrete tilt wall to an existing slab. My co-worker says that I can use this exception, but I say that it doesn't apply since it has to be used with a flexible diaphragm. Since we're connecting our wall to a slab then we don't have a flexible diaphragm and therefore can't use that exception.

Thoughts?
 
Your co-worker is incorrect if you are not using 12.11-1. The out-of-plane wall anchorage load already applies an increase on the loads, .8/.4 = 2.0, which is similar to the exception to ductile failure by reducing the anchor capacity by .4, 1/.4 = 2.5. So if you need to retrofit a rigid diaphragm and are not using 12.11-1 you need to comply with the ductile requirements.
 