2-winding Transfromer with Buried Delta Tertiary Winding

Status
Not open for further replies.

jliu1

Electrical
Jul 12, 2002
23
Hi;

What is the impact of 2-winding transformer Buried Delta Winding to the system response? Does it have to be modeled for Load Flow, Short Circuit or Motor Starting studies?

Thanks
 
Replies continue below

Recommended for you

For calculating line-to-ground fault currents you will certainly need to account for the delta tertiary. For Power Flow and motor starting, not as much impact.
 