Copper phone lines in conduit with power wires is a bad idea, because the phone wires are not insulated like the power wires, which >I think< is what the NEC would require to make it allowable.
Running fiber through dedicated conduit should be okay, but running it alongside power wires is a bad idea because it won't like being kinked at the boxes, where no room is provided. As sure as you specify only bent conduit for direction changes, somebody will put in a cast elbow.
Mike Halloran