1170.3 Snow Actions - Obstructed Sloping Roofs

Status
Not open for further replies.

m_struct

Structural
Nov 11, 2020
64
Looking at a two level residential building with a 45 roof. The client would to open up the building with the house by raising sloped roof to approximately 20 degree.

Snow_Loading_pompj2.png



As the snow will now be obstructed, per figure 7.2 1170.3, it appears the existing truss would be exposed to a significantly larger snow load. For slopes greater than 10 degrees, do the formulas in figure 7.2 get reduced by factor (60-∝)/50 as is done for Figure 3? Refer below.

Snow_Loading_shape_coefficient_mdudyh.png
 
Replies continue below

Recommended for you

My interpretation is that the reduction only applies where it is specifically noted for a specific case. So it does not apply to figure 7.2(c) situations.

Clause 7.4 specifically applies only to abrupt steps as shown in figure 7.3 which isn't your particular case.

 